Hillary123 Posted September 19 Share Posted September 19 Hi, I am generating an 8760 and would like for it to only include positive generation values (no consumption during night time hours for any reason). I have turned off the auxiliary losses all together, but I am still getting negatives. What other losses are causing these negative values? Is there any way that I can avoid having any negative values all together? Ideally, I would like to 8760 to reflect generation losses due to daytime auxiliary losses (or any losses that are a result of using the sites own power production to cover electricity needs), but i do not have to reflect losses due to pulling electricity from the grid. Is this possible? Link to comment Share on other sites More sharing options...
Linda Thoren Posted September 20 Share Posted September 20 Hello, If you have defined a transformer that is not disconnected during the night, the negative values could possible come from the Transformer losses. Transformers have a constant iron loss, even if no energy is being produced. To avoid this, you need to enable 'Night Disconnect', in the Ohmic Losses window. Link to comment Share on other sites More sharing options...