Hi, What exactly are you trying to model? Are you focusing on production during peak demand hours or the price difference between on-peak and off-peak periods? In the economic evaluation, you can define different prices for on-peak and off-peak periods. You can also always generate an hourly output file with the relevant parameters and analyze the data in Excel or other external tools.
-
INCENTIVOS FISCALES EN ANALISIS ECONOMICO
Linda Thoren replied to Andrés Sánchez's topic in Simulations
Hello Andrés, Please note that the language in this forum should be English. You can find a detailed explanation of all the possible inputs and parameters for the economic evaluation in the following YouTube tutorial: Kind regards -
PVsyst does not show Plane of Array Irradiance AFTER backtracking
Linda Thoren replied to Ahmad's topic in Problems / Bugs
Hello, Indeed both GlobInc and GlobEff will be in the collector plane at the position with backtracking if backtracking activated. You can export also the phi angle to verify the position of the trackers every hour. -
Simulation of the temperature of photovoltaic modules
Linda Thoren replied to FGsilentd's topic in Simulations
Hello, Indeed, if there is no production, the temperature of the modules are simply not calculated and put to 0. This has no impact of the result of the PV production since no thermal inertia is considered for the hourly simulations. For a more elegant output file we will considered changing this approach. For your evaluation you could consider the 0 as null and exclude from your average, or replace them with for instance the ambient temperature. Thank you for your input. -
Define power sharing with less number of mppt inputs used
Linda Thoren replied to faculuc's topic in Simulations
Hello, In general, you can define multiple MPPTs per sub-array (as long as you have a multiple between the number of strings and MPPT inputs). Indeed you have this constraint in the current version that you can not have empty MPPT inputs. To get around the constraints in PVsyst, you could modify the number of MPPTs in the OND file, though this might impact other behaviors of the inverter and you should adjust all the parameters to correspond to the use-case you are referring too. The following youtube video further explains the MPPT and Power sharing: -
Hi, No it is today not possible to include that in the original simulation. If you choose to simulate both sides as front sides, that can indeed be simulated in the same variant (with the proposed work around of modifying the .PAN files) You are right, the thermal losses only consider front side irradiance, we will look into this. Kind regards
-
Hello Luis Zimmermann, In PVsyst, the beam and diffuse components and the rear side of a vertical bifacial PV system are calculated similarly as on the front side, by computing the integral of the visible sky. For the rear side irradiance, this is done using a 2D intersection method, same as the "unlimited shed" field type. If the layout is done in the 3D scene, the visible sky is instead in 3D. With bifacial systems, the view factor model also estimates the contribution of ground reflection to the front and rear side (not considered in mono facial simulations).
-
Hello, In the economic evaluation, you can include hourly tariffs to assess the financial benefits of a peak shaving strategy. You can in the peak shaving strategy specify the hours when you allow for the battery to discharge and inject to the grid and calculate the revenue based on the corresponding tariff rates. However, the system does not work in reverse—economic data cannot be used as an input to control battery storage behavior.
-
Grid-connected PV plant with battery storage and no self consumption
Linda Thoren replied to Vasil Janevski's topic in How-to
Hello, Indeed the peak shaving is not design for this exact purpose. With the peak shaving strategy you will only store the energy above the set grid limitation. Setting a lower grid limitation will allow to charge the batteries and then you can set the specific hours for when you want to discharge the batteries. Indeed the discharge of the batteries will also be limited to the set grid limitation threshold. -
If you have less production, there will be less energy to charge the battery with, no matter the size of the battery. But it could indeed also depend on the charging and discharging power
-
Hello, The system is not completely the same before the battery (you have a 9.2% loss to the right compare to 2.3% to the left), thus you have less solar production to the right. Also have a look at for instance the charging and discharging power. Kind regards
-
Indeed this is a limitation of the bifacial model today. A possible workaround, is to modify the .PAN file and place two panels back to back. By creating separate modules for the front and rear—each with a bifaciality factor of 0 (and adjusted properties, e.g., lower power, no AR coating for the rear)—you could place them back-to-back in the 3D scene and simulate the system using the Module layout. This wouldn’t fully replicate real system behavior, and on clear days electrical shading losses might be underestimated due to the fact of having two panels instead of one. This in not necessary a recommendation, but could work as a test to evaluate the shadings for the backside. Otherwise, for the estimation of the electrical shading losses in general for a vertical EW system, the irradiance distribution on the rear side should be roughly as uniform as on the front. This means that, in principle, the rear mismatch factor should be set to zero, as it only accounts for additional non-uniformity on the rear. However, since PVsyst currently calculates electrical shading losses only for the front side, using the rear mismatch factor as an approximation for rear-side shading losses is reasonable. That said, determining whether 5% is an accurate value is difficult, as it depends heavily on system geometry (row height, spacing, etc.). As a first approximation, it would be best to adjust the rear mismatch factor so that its corresponding losses in the loss diagram match the electrical shading losses multiplied by the bifaciality factor.
-
Can someone please explain the diagram loss for bifacial?
Linda Thoren replied to RobSolar's topic in How-to
Hello, Indeed this is not very straightforward. The irradiance on the rear side is renormalized to the 4806872 m2 of collectors after the View Factor (1111 -73.71% -81.34% * 14897331/4806872 +15.6% +0% -9.9% results in 176). This further explained in the help page below: https://www.pvsyst.com/help/project-design/bifacial-systems/bifacial-systems-results.html