  1. Dear Emi,

    In your configuration you must define orientation1 and 2 with "mix 1 and 2" the define your sub-array N°3 as orientation N°3.

    This will allow you to position three orientation on two MPPTs like the example below :

     

    image.png

  2. Dear Ynesse, 

    VmppNom: Nominal MPP voltage is sometimes specified by the manufacturer.

    In this case this may be an indication for the optimal number of modules in series.

    Weakly used in the sizing tool in the present time

     

  3. The ohmic losses behave in a quadratic way with the array current:   Ploss = Rw · Iarray².

    Now if the array is not operating at  STC, the wiring loss fraction   will become:

    Ploss / Parray  =   Rw *  Iarray²  / (Varray * Iarray)   =  Rw * Iarray / Varray.

    i.e. proportional to Iarray. This means that at half the irradiance (half the current), the wiring loss fraction  will be half, etc. Therefore the Wiring energy loss has to be evaluated at each hour of the simulation, and accumulated in terms of energy.

    The final result of the Ohmic wiring loss (in terms of percentage) as shown on the loss diagram will be from this hourly energy balance. It is usually of the order of 60% of the Loss fraction specified a STC.

     

  4. Dear Detroit Solar,

    Thank you very much for your interest in a PVsyst training.

     We propose some online personalized sessions in the form of Consulting and PVsyst project support, to answer specific requests (no standard sessions for the moment).

     If you are interested in this service, you are kindly requested to request an online quote here: https://www.pvsyst.com/consulting/

     We will establish a program relevant to your specific requirements.

    Our sessions last for 2 hours (including participants question time) and are charged CHF 700.-

    Our online sessions are limited to 5 participants per session.

    We do not provide any guarantee relating to your simulation results.

     In the meantime, we have designed several online video tutorials which we invite you to watch:

    https://www.youtube.com/channel/UCMzsEWHk3f7XD_dg1lngmzg  or access our online course at: https://vimeo.com/pvsyst

     If you have a technical question, please feel free to send an email to support@pvsyst.com

  5. The IAM model is defined with the PV module parameters, page "Additional data > Customized IAM".

    Here you should define the glass surface type, and PVsyst will attribute the corresponding IAM model.

    The PAN file of low light measurements, apart from the integration of this data, is extremely sensitive.

    The reference is that at 200 W/m2, the real efficiency is -3%.

  6. If you have made an orientation and azimuth choice with an annual irradiance optimization, the first estimates appear. When you click on OK and then return to the window, PVsyst does not change the Azimuth and tilt values but does not show the graph by default in Winter (the most unfavorable) this does not change the simulation or your parameters

×
×