cyoung Posted November 13, 2020 Share Posted November 13, 2020 I'm simulating an off-grid system with a battery and backup genset but i cant figure out how to change the SOC trigger level for the Generator Startup.In the PVsyst Report this is listed as "Battery Management Control" "Back-Up Genset Command SOC = 0.15/0.45"I interpret this as start generator at 15% and stop at 45%I would like to change this to start at 30% and stop at 55% to reduce battery wearHow do i change this?Thanks Link to comment Share on other sites More sharing options...
cyoung Posted November 23, 2020 Author Share Posted November 23, 2020 Answered my own question,The settings i was looking for are under Main Parameters --> System --> PV Array Tab --> Controller (Open) --> Thresholds Tab Link to comment Share on other sites More sharing options...