  2. Is it possible to set inactive panels? Is it possible to run a simulation for FIX when there is a tracker running above them? And get 2 simulations at the same time? This is also important at a global radiation level and not just in production - how do you do it?
  3. I want to run 2 simulations in parallel, one of a single-axis track at a height of 2 meters, and static panels on the ground, and I want to calculate detailed parameters for each of the cases - that is, to know how much radiation lands on the static panels, but the panels in the track work above them. How do I do that?
  4. Hello, Indeed filtering out these two variables should be sufficient to remain compliant with the ASTM 2848-13 standard
  5. Yesterday
  6. Hello, I am running a PV capacity test per ASTM2848-13 and it is important to filter out any data where shading is present. I am struggling to interpret the shading losses per the 8760 outputs. I have FShdBm and ShdBlss. Is there shading whenever FShdBm is < 1 and whenever ShdBlss > 0? Should I use any other 8760 outputs or is this sufficient? Thanks.
  7. Your data looks slightly shifted in time, did you define the time shift correctly when first importing your data? https://www.pvsyst.com/help/meteo-database/notes-on-meteo/meteonote7-time-shift-in-meteo-files.html?h=poa#time-shift-correction-when-importing-data When importing POA data, PVsyst will first transpose it to GHI and DHI which are required for shadings calculations. POA will be computed again during the simulation. Slight variations are therefore possible between input POA and GlobInc, but not to the extend you are observing.
  8. Last week
  9. I am trying to compare the the Plane of Array Irradiance (POA) in w/m^2 i get from scada with the Global Incident in Coll. Plane from the PVSyst output knowing that the meteo file i used in simulation is generated using the scada data imported as a custom file so as i imported the POA to the PVSyst i expected that the POA should be identical with Global Incident in Coll. Plane but there is a differences in months starting from may to november attached a sample of the issue can any one explain why is this behaviour thank you in advance
  10. Indeed all tables need to have the same width and you need to have pitch (thus more than 1 row) to calculate the bifacial gain. A possible workaround for the issue of only having 1 row, is to duplicate the scene further away so that PVsyst can detect a pitch. Verify that the tables are well aligned so that indeed PVsyst detects the pitch in bifacial window. Note that the amount of tables in the 3D scene will be double what you have defined in the system and this will create a warning. You can increase this limit in the advanced parameters. In the first PVsyst welcome window, click “Settings” and “Edit advanced Parameters” and find the parameter that triggers the error message – “Shadings: absolute maximum shading/field area ratio”. This will allow you to run the simulation
  11. Hello, Can you also please share the Water Needs section and the pumping hydraulic circuit? Regards,
  12. Does that affect your summer days only? If yes, that's the sign of a wrong DST definition https://www.pvsyst.com/help/meteo-database/import-meteo-data/custom-meteo-files/conversion-protocol.html#summer-time-daylight-savings Otherwise, issues can arise from a discrepancy between your real tracker angle and the one computed in the PVsyst orientation. Do you have any way of comparing your tracker angle and the PVsyst tracker angle?
  13. Hi, Please stop rounding numbers to 0.1 and give us 0.01. Rounding makes for inconsistent values, and it's not possible to know whether a calculation has been done correctly. (I think sometimes a calculation does use the parameter value as entered, but the report shows it in tenths.) I've been unhappy with this for a long time, but I am motivated to write now because of difficulty I'm having interpreting the representation of mixed blocks as broken down over multiple MPPTs. There are 20 MPPTs used, so a resolution of 0.05 is needed. 75% of the entries are shown rounded and the totals don't add up. (See illustrations.) Thanks.
  14. Dear PVsyst Team, I am currently designing a solar-powered submersible pumping system; however, I am encountering challenges during the system definition stage; specifically in selecting and configuring a pump that meets my design requirements. As a result, I have been unable to successfully run the simulation. I would greatly appreciate your support in reviewing my setup, helping me define a suitable pump configuration, and enabling the simulation to run correctly. Thank you in advance for your assistance.
  15. Hi everyone, I enter the measured POA irradiation for the whole year based on every 10 min measured irradiation, we got shifted 2 hour POA irradiation for the results during summer time, how to solve this, I've seen that the GlobInc values sometimes lower from the POA values input.
  16. Earlier
  17. @Linda Thoren, Thank you for your suggestion. I've incorporated that, but after that, I am getting the new error as below. I assume, this was because of the 4 wide carport tables. To resolve this, I created another orientation for the 4 wide tables and created a separate sub-array too. But, then the new error was as follows. I think this is because there's only a single table of 4 wide array. Is that right? And what is the solution for this issue?
  18. Hi, The issue most likely comes from the definition in the 3D scene, if each panel is defined individually rather than as a table. As the red message in this window indicates (though not very clear so this can indeed be confusing), you can play with the shed's parameters as you like for parametric analysis, though the simulation will be done with the defined values in the orientations window and the table size in the 3D scene, only the pitch and number of rows can be overwritten. To solve this, you need to define tables rather than individual modules. If you are importing the tables from another 3D software, make sure you indeed draw full tables (as the alternative to the right), and PVsyst then normally will fill the total area with individual modules and the area will be considered a table.
  19. Hi @Michele Oliosi and @Linda Thoren, I am working on a carport system and trying to model the Bifaciality correctly. The snip of the system and the bifacial modelling from PVsyst are attached below. I have 6 (majority) and 4 modules in portrait orientation in a carport table. But, the bifacial system definition shows the pitch and shed total width as 2.28m, which is only the length of a single module. When I try to model the system as per the actual array, i.e., 6 modules in portrait, making the shed total width 13.72 m and the effective pitch between the two arrays approx. 19.92m, the system definition brings back the shed total width to length of 1 module, i.e. 2.28m. Am I modelling the bifacial system correctly or is there something I am missing?
  20. Hi, I am modeling a complicated array that uses 6 different modules, some mono- and some bifacial. We are supposed to run strings of as many as two bin classes of monofacials and one class of bifacials all into the same inverter. This inverter model (rated at 4000 kW) has a single MPPT. On top of everything else, the inverter loading ratio is 1.5, so clipping will be important. What is the best way to represent this? I have read the information about "power sharing" in the manual and watched an instructional video. These both centered on how to represent multiple MPPTs in the same inverter separately (which is the opposite of power sharing). I know two ways to combine modules of the same type but different bin classes This is by creating an "equivalent block" by picking the dominant module and adjusting either the number of modules or MQF to get the correct DC capacity. The other is to break up the inverter. The former has the advantage of treating all of the DC power together when computing clipping. The second is more explicit, but would seem to miscalculate the clipping. I know one way of mixing mono- and bifacial modules. That is creating an "equivalent block" where the capacity of the bifacial modules is multiplied by an effective received irradiance factor and then following the standard "equivalent block" method above using a monofacial module. Maybe the two types can just be combined in PVsyst 8? Otherwise you can break up the inverters again and put the monofacial and bifacial modules in different variants. (Again, this would seem to compute clipping incorrectly.) So back to the original question: What would be the recommended/most accurate way to model these inverter blocks? Thanks. Too many Frankenstein systems these days!
  21. With Peak shaving, the strategy is relatively simple: charge the battery with excess energy and discharge the battery into the grid up to the grid limitation value. You could set up your system to start discharge during the night (i.e with PV zero production). In this case, you will discharge at the max inverter power (20MW) until the battery is empty. To ensure your battery is fully charged each day, you can use the power shifting strategy instead Using the "Fixed charging power before exporting" will prioritize battery charging before grid injection. This won't guarantee a full 40MWh/day of charging if the PV production is lower than that, but you should be closer to your target. This will probably lower your overall PV production though, since the battery will be more likely to be fully charged when your PV production reaches the grid limitation.
  22. Hi Robin, Thanks for the confirmation. Should there be a customer requirement for the batteries to be of capacity 20MW and to discharge for 2 hours on a daily basis, is it even possible to simulate this in PVsyst?
  23. With the Peak shaving strategy, you will indeed put any excess production into the battery with respect to the charger max power and battery state of charge. In these conditions, you can charge your battery up to 20MW, but only if the total AC power is 50+20MW. Your system will always output less than 70MW (max clear sky production being estimated to 68.23MW), but will also charge for more than 2 hours a day, so your daily charging energy will be somewhere between 0 and 40MWh/day. The actual energy will depend on the weather and battery state of charge at the beginning of the day, so you cannot predict the charging/discharging energy based on the max charging power.
  24. Hi, I am trying to simulate a 75MWp/50MWac PV + 20MW/40MWh BESS system with grid limitation at 50MW in which the excess is used to charge the BESS. However, the requirement is to ensure that the BESS is able to fully charge and discharge 20MW for 2hours daily. Theoretically this should amount to an average of 1.2GWh per month or 14.4GWh per year. However, based on the results obtained, the EBatDis is only at 4.3GWh per annum. Storage strategy is set to Peak Shaving with the following parameters Please advise if there is any settings changes to be made to achieve desired outcome.
  25. Hi, Several of the reference links on the help page regarding the First Solar Spectral Correction appear to be broken or point to retired URLs. Page URL: https://www.pvsyst.com/help/physical-models-used/pv-module-standard-one-diode-model/firstsolar-spectral-correction.html Updating these links would be helpful for users looking to verify the underlying physics and validation of the spectral model. Thanks.
  26. Sorry no news yet, we are looking at update 8.2 at the moment... but that could change still.
  27. Dear all, I am coming back to this old topic to see if there is news on this subject of 3D scene + dome + bifacial modules
  28. Hello, The losses due to the wind stow position of the trackers do not directly appear in the loss diagram. The only way to evaluate these losses would be to run a simulation without wind stow and evaluate the difference between the simulation. If you are using sub-hourly data and the sub-hourly clipping correction model, you find the additional clipping correction printed in the loss diagram. Im not sure what you mean by terrain loss? With the 3D scene, you can evaluate the mutual shadings that might appear due to the terrain, as well as shadings actually caused by the terrain, these will be shading losses. Shadings from shading objects or the terrain will be grouped together. To evaluate them separately, you would need to run several simulations with and without the different shading objects. You can also import a horizon profile to evaluate far shadings.
