HV transformer loss > MV transformer loss


Daksha B

Recommended Posts

Could someone help me with why my simulation results look like this? I have never seen the HV xfmr loss > MV xfmr loss. My inputs are - 

MV xfmr loss = 0.87% + 0.13%

HV xfmr loss = 0.45% + 0.05%

image.png.1ba6ad70e66edbd240b6a25f110c3760.png

 

Could it have something to do with weather file/weather at the site location? 

Link to comment
Share on other sites

IIn PVsyst, the transformer losses are defined as a sum of

- the ohmic losses, proportional to the square of the current or power, calculated at each hour of the simulation. The annual ohmic loss value  is not identical to the specified loss fraction, which is specific to a reference power. See the help "Project design > Array and system losses > AC ohmic loss from inverter to injection point".

- the iron loss, a fixed constant loss, permanent as soon as the transformer is connected to the grid. This may give a high contribution  as it is permanent and doesn't depend on the PV production. See the help "Project design > Array and system losses > External transformer losses"

 