Abdel Posted April 4, 2021 Posted April 4, 2021 Hi, I have problem in my design but I don't know what is exactly the problem , the system consists of 154 KW DC power (Longi 370W PV modules) with 3 Sunny Tripower core 1 inverters of 50 KW (total 150KW).As shown in the error message " The array Voc at -27 is greater than the inverter absolute input voltage". the location of the design is located in Finland and in winter the temperature can reach until -30 , so I can't rise the temperature. When I tried to decrease the the number of modules in series , the system gave me error message "8 inputs with 1 string and 10 inputs with 2 strings , Consider disabling use of multi-MPPT feature for ensuring power sharing on each input" So , Can PVsyst team help me with any hint to solve the problem ?
dtarin Posted April 5, 2021 Posted April 5, 2021 Disable mppt share. Set to 14 modules in series, 30 strings.