ESL_2010 Posted March 28, 2019 Share Posted March 28, 2019 Hi folks,I'm modelling a simple grid-connected PV system and have added a battery under the "weak grid" scenario.In this location however, it is not permitted to export any power back to the grid. When I try to set a limit using Energy Management > Grid Power Limitation, it does not allow me to set the grid power limitation to anything less than 1kW.The manual does not suggest that there is a requirement for grid export to be >0. Can anyone confirm if this is indeed the case, whether I'm just doing something wrong, or is this a bug? Link to comment Share on other sites More sharing options...
André Mermoud Posted April 17, 2019 Share Posted April 17, 2019 Perhaps you are using an old version.In the Weak grid definitions you have this option:Group "Operating conditions", checkBox "Allows solar injection into the grid." Link to comment Share on other sites More sharing options...
ESL_2010 Posted April 17, 2019 Author Share Posted April 17, 2019 Perhaps you are using an old version.In the Weak grid definitions you have this option:Group "Operating conditions", checkBox "Allows solar injection into the grid." Thanks André - I had indeed failed to spot that checkbox even though it was obvious once you pointed it out. Link to comment Share on other sites More sharing options...