wilsonxsun Posted March 17, 2016 Posted March 17, 2016 Hi all, I am trying to run a simulation of a 100kW system. The system contains 1 central inverter with 1 MPPT. However the panels have 3 orientations that are slightly different to each other. I understand with 2 orientations, i can use the mixed #1 and #2 option, however what if there were 3 orientations connected to one tracker, is there a way to run an successful simulation? Please let me know. Thank you.
André Mermoud Posted March 20, 2016 Posted March 20, 2016 PVsyst only treats the mix of 2 orientations on a given MPPT input. If you have 3 orientations, you should define an average between two of them. The results will not be very different.
solar_dummy Posted February 24, 2020 Posted February 24, 2020 PVsyst only treats the mix of 2 orientations on a given MPPT input. If you have 3 orientations, you should define an average between two of them. The results will not be very different. When do you mean with average between them? Lets consider an extreme case where we have 2 orientations: -90S and +90S. The average would be 0S (??) but the result couldn´t be more misleading.I am trying to compare mismatch losses of central inverters and string inverters for minor differences in orientation.Thanks in advance.
André Mermoud Posted March 4, 2020 Posted March 4, 2020 The simpler way is to redefine your inverter with 3 MPPT inputs, and attribute one sub-array to each input. The mismatch between orientations (i.e. between strings in different orientations) is usually very low (a fraction of %). You can check this by defining one sub-array with a "mixed" orientation. Here the calculation is correct, as it uses the mix of both I/V curves.
H.Tannous Posted June 20 Posted June 20 Hi I have three orientations and would like to use 1 invertor with 3 MPPT inputs for that but I am not sure how to assign a single invertor to all three subarrays. I tried selecting the same invertor for each orientation with 3 MPPT but kept getting the following message: "you should define at least one string per inverter or MPPT input? Can you please advise? Kindly, Hadi
André Mermoud Posted June 21 Posted June 21 In your Subarrays definitions, you have defined 3 MPPT in each sub-array. If so, you should indeed define at least 3 strings in each subarray. Now in your case you have one string per Subarray, so that should define one MPPT input in each subarray.