Zahra Posted August 16 Posted August 16 Hello, I am conducting an experimental study on the degradation of a Building-Integrated Photovoltaic (BIPV) system, which uses a single semitransparent Photovoltaic (STPV) module on a facade at a 90-degree tilt connected to an EcoFlow portable power station that functions as both the inverter and battery. I am seeking guidance on the most accurate way to model this setup in PVsyst, as I have two primary questions: First, the setup is not connected to the grid and the EcoFlow's battery capacity is a fixed component that was not sized based on an energy demand profile, is it more appropriate to model this system as grid-connected rather than standalone? Second, given that the EcoFlow unit combines the inverter and battery, what is the recommended approach for modeling it? If I need to represent it as separate components, I would appreciate guidance on the key technical parameters that are essential for an accurate simulation.
André Mermoud Posted August 18 Posted August 18 The Stand alone systems simulation in PVsyst is based on a balance between the PV production, the user's consumption and the intermediated battery for ensuring a match at each instant between these two energy systems. Therefore if you don't define the user's needs, the simulation cannot work, and I really don't see what you want to obtain as a result. Now if you consider this as a grid-connected system with storage, this should be a self-consumption system, and the problemremains the same: without self-consumption definition this doesnt make sense. You can indeed consider a grid-connected system, without storage, for the evaluation of the possible PV yield. This will not involve the battery. The battery behaviour is obviously dependent on when you will consume this energy, therefore on the user's needs definition. i
Zahra Posted yesterday at 12:57 PM Author Posted yesterday at 12:57 PM Hello André, Thank you for your response. As I mentioned, I used an EcoFlow unit in my setup, which includes both an inverter and a battery. I am planning to add a heater as the load. For clarification, do you think it is appropriate to model this system as grid-connected, even though it is not physically connected to the grid? Also, since the EcoFlow integrates the inverter and battery, what would be the recommended approach for modeling it? If it is OK to represent them as separate components, I would appreciate your guidance on the key technical parameters needed for an accurate simulation. Best regards, Zahra
André Mermoud Posted 15 hours ago Posted 15 hours ago The EcoFlow is a grid-tied inverter, which can only be used (in PVsyst) in a grid-connected system. Now if you want to use it in a stand-alone system - which is probably more suited for your very special use - you should define it as a "Controller for Stand-alone" in the database. But the problem of the user's needs definition remains the same: you have to define it, whatever the way you are using the produced energy. The battery needs to "know" when it has to be charged or discharged.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now