I am trying to understand how to enter the MV line loss percentage. Let me explain an example:

I have a circuit collecting 3 Power Stations with 1 transfo each. The calculated power losses of the MV line are:

PS1-PS2: 0,05%

PS2-PS3: 0,03%

PS3-SET: 0,07%

In total I have a power loss of 0,15% but, when entering the data into PVSyst should I enter the mean between each power station and substation (0,05%) and assume there are 3 transfos as shown below?

image.png.22cda0076674d5864cc3d22785cac851.png

Thank you very much in advance!

Edited by jonipa
Link to comment
Share on other sites

I don't understand well what are your power stations, and what you mean by "PS1-PS2", PS2-PS3" and "PS3-SET".

If these are  transformers in series, PVsyst only treats two stages, i.e. a  section  "Inverter => MV transfo", and a section "MVTransfo => HV transfo". The wire between HV transfo and  Injection is indeed not taken into account (this is a weakness of PVsyst). In this case the losses (in percentage) should indeed be added, as they concern the same power or energy flux.

Now when you define 3 MV transfos as you did, this means 3 circuits  "Inverter => Transfo" in parallel. In this case the losses have obviously to be added in terms of energy (kWh). And the loss in percentage will be the total loss in energy, divided by the total transferred energy.

Please carefully read the Help   "Project design > Array and system losses > AC ohmic loss from inverter to injection point"

And also  "Project design > Array and system losses > External transformer losses"

 

 

 

Link to comment
Share on other sites

Thank you André, so if I understand right it would be really helpful to confirm the following:

  1. What do you mean with "The wire between HV transfo and  Injection is indeed not taken into account (this is a weakness of PVsyst)" I understand if I enter the losses for the High Voltage line inputs they are taken into account right?
  2. image.png.eb2470101f649112df280376415ae80a.png
  3. I am still not sure how to manage the losses for different MV circuits in parallel with a number of MV transfos in series each.

Taking a look to the Help you mention:

image.thumb.png.e23fb47ac7a4ac991b2dab13ec8d0a16.png

In the last line, it mentions defining an average lenght, so considering my input are the power losses, I should define an average loss for each transfo and mantain the total number of transfos of the system. Is this right?

As an example, if I have two parallel circuits with 3 transfos in series each, and the total power loss of both circuits is 0,6% I should enter and average loss of 0,1% for each transfo, right?

Thank you very much.

Link to comment
Share on other sites

3 minutes ago, jonipa said:

As an example, if I have two parallel circuits with 3 transfos in series each, and the total power loss of both circuits is 0,6% I should enter and average loss of 0,1% for each transfo, right?

Thank you very much.

Your total power loss is 0.106%. The first segment carries 1/3 of the total power. The second segment carries 2/3s. The final segment carries 100%. That is total loss for the entire plant. Enter that for the MV ohmic loss %.

Link to comment
Share on other sites

Either is correct, you can enter 3 and average the no-load and full-load loss, or add them into one. Since you have combined the MV ohmic losses into a single loss, I suggested to do the same with the transformer, perhaps a bit more accurate instead of averaging them, since pvsyst is using the total power into the transformer 

Link to comment
Share on other sites

Shouldn't I enter 3 transfos anyways so that I let PVSyst know that the averaged MV line losses repeats 3 times? If I only enter 1 transfo I am afraid the total MV line power losses will only be considered 1 time. 

Link to comment
Share on other sites

The total ohmic loss is a single loss, the sum of the weighted averages. This would correspond to a single transformer loss, the sum of the transformer losses.  If you wish to use three then use the straight average. My preference would be to use the former. Run both and check the difference 

Link to comment
Share on other sites

Right, I'll check. Summarizing, I understand the two options as follows, seeming 2 as the more accurate one:

  1. If input the total number of transfos: Average the total power losses (Ptotal / num transfos).
  2. If input only one transfo: Input the total power losses and add up all the no-load loss, full-load loss and power in the transformer data.
Link to comment
Share on other sites

  • 4 months later...
  • 2 weeks later...

The number of transformers doesnt really matter in PVsyst, it will create a single transformer for the transformer loss calculation. For ohmic losses, calculate the total weighted average power loss for the entire system and use that for the medium voltage line input. From your previous post, if the total power loss of both circuits is 0.60%, that is what you will enter for loss fraction at stc (assuming that value was calculated at stc conditions). Regarding your previous post , the average loss would not be 0.1% for each transformer. In each circuit, each "leg" is carrying a different current value. The first leg is 1/3, the second is 2/3, and the last leg is 3/3. 