Posted

Hi, I configured PF=0.95 in Energy managment but when I check the Sytem design the inverters were not affected by it and so Ratio dc/ac is calculate as PF=1.

image.png.74cfd09553e9e1b79ef810cabc335189.png

 

image.png.442f5fa67a135d8241dbe8b7ee4719fd.png

Posted

It does not update DC/AC ratio. In order to check, look at the 8760 at the inverter output. Ensure that PF is being applied such that it matches the PNOM definition in the OND file. 