solarysnrg Posted February 17, 2022 Posted February 17, 2022 In a system connected to the grid with backup batteries, the energy balances are not consistent!EDirUse+EBatCh+E_Grid > E_Avail ( much greater )
Bruno Wittmer Posted February 18, 2022 Posted February 18, 2022 The variable EDirUse containds already E_Grid. It represents all the energy that does not go through the storage:E_Avail = EDirUse + EBatCh
solarysnrg Posted February 18, 2022 Author Posted February 18, 2022 The variable EDirUse containds already E_Grid. It represents all the energy that does not go through the storage:E_Avail = EDirUse + EBatCh But is non correct! If the energy is sold to the grid it is not directly used;
Bruno Wittmer Posted February 24, 2022 Posted February 24, 2022 This is a matter of definition. 'Direct Use' in this context just means that the energy did not go through the battery.You can compute the energy that went directly from solar to self-consumption by subtracting E_Grid from this value.