Hi experts,

Why PVsyst compares between the array Isc and the inverter maximum PV current input not the maximum Isc of the inverter.

For example: an inverter has 14 inputs, Isc max input of 140A while Imax PV input is 120A so, safely it can take on 14 strings (Isc of the panel is 8.98A @ STC) but it shows the error as in picture attached.

Since I'm considering Isc of the array, it should take Isc input of the inverter into account.

Any explanations ?!

Sincerely,
Eng.Mohammad AlKour


Attachments:
File comment: Error
Screen Shot 2019-01-03 at 11.59.46 AM.png
Screen Shot 2019-01-03 at 11.59.46 AM.png [ 43.23 KiB | Viewed 357 times ]
Top
   
PostPosted: Fri Jan 11, 2019 7:04 pm 
User avatar

Joined: Tue Oct 18, 2016 3:31 am
Posts: 170
This can be overridden in the OND file. Under Contractual specifications, uncheck the box next to "Maximum PV Current". This has no impact on the simulation results.


Attachments:
inverter contractual conditions.jpg
inverter contractual conditions.jpg [ 50.36 KiB | Viewed 245 times ]
Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 2 posts ] 

All times are UTC+02:00


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Limited