Author:  m.alkour [ Thu Jan 03, 2019 10:05 am ]
Post subject:  Isc vs Imax input of Inverter

Hi experts,

Why PVsyst compares between the array Isc and the inverter maximum PV current input not the maximum Isc of the inverter.

For example: an inverter has 14 inputs, Isc max input of 140A while Imax PV input is 120A so, safely it can take on 14 strings (Isc of the panel is 8.98A @ STC) but it shows the error as in picture attached.

Since I'm considering Isc of the array, it should take Isc input of the inverter into account.

Any explanations ?!

Sincerely,
Eng.Mohammad AlKour

Attachments:
File comment: Error
Screen Shot 2019-01-03 at 11.59.46 AM.png
Screen Shot 2019-01-03 at 11.59.46 AM.png [ 43.23 KiB | Viewed 1267 times ]

Author:  dtarin [ Fri Jan 11, 2019 7:04 pm ]
Post subject:  Re: Isc vs Imax input of Inverter

This can be overridden in the OND file. Under Contractual specifications, uncheck the box next to "Maximum PV Current". This has no impact on the simulation results.

Attachments:
inverter contractual conditions.jpg
inverter contractual conditions.jpg [ 50.36 KiB | Viewed 1155 times ]