 Post subject: unbalanced MPPT
PostPosted: Wed Mar 24, 2021 11:05 pm 

Joined: Wed Mar 24, 2021 10:34 pm
Posts: 11
Hi, I am a new user of PVsyst and I hope to get help or hint for my design.
I want to design PV system that consists 38 KW PV modules (Longi 370W) and 2 inverters Fronius 20 KW. my problem I don't know how I can design the system using "unbalanced MPPT". I have defined 2 sub-arrays, one for main input and another for secondary input, I have set 4 strings with 19 PV modules each string for main input and 4 strings with 7 PV modules each string for secondary.
First question: Is this correct ?
Second question : does this mean that the number of strings for main and secondary input for one inverter or PVsyst will considered for two inverters ?


Attachments:
Capture.PNG
Capture.PNG [ 311.61 KiB | Viewed 273 times ]
Top
   
 Post subject: Re: unbalanced MPPT
PostPosted: Thu Mar 25, 2021 9:48 am 
User avatar

Joined: Thu Sep 26, 2019 10:47 am
Posts: 16
Hi,

Inverters with Unbalanced MPPT inputs

Some special inverters (namely in the Tripower series of SMA) have 2 MPPT inputs with very different powers. In practice this is very useful as you can define an array without much constraints about the module number on the main input, and one string with the remaining of your modules to be installed - whatever their number - on the secondary input. This feature is part of the Inverter's definition.

With these very special unbalanced inverters, when defining a sub-array you will have the choice between "Main" and "Secondary" MPPT inputs.

In principle you should define sub-arrays for the same number of "Main" and "Secondary" inputs (i.e. use all the available inputs). However the button "adjust" gives the opportunity of not using the secondary input. Please check with the manufacturer that this is really possible with the real inverters you are using.

At the design time, the nominal powers of each input are evaluated according to the maximum currents specified for each MPPT inputs. This may sometimes lead to unacceptable overload losses. If this warning is red (error), you have to increase the allowed overload energy loss in the "Project's" parameters (button "Albedo-Settings").

At the Simulation time, the power sharing (as mentioned above for normal MPPT inputs) is automatically performed as function of the PV modules connected in each sub-array. The Pnom of each MPPT input is evaluated just before the simulation.

Example of use (tutorial):

Suppose you have to build a PV system using 155 PV modules of 250 Wp, i.e. 38.75 kWp.

1. - Choose the inverter(s), according to a reasonable PNom ratio of 1.25: you need inverters for PNom(ac) = 38.75 kW / 1.25 = 31 kW. 2 inverters with unbalanced MPPT, of PNom = 15 kW should be well suited.

2. - In the "System" part, Define 2 sub-arrays,

3. - First one: define "Main" input with 6 strings of 20 modules (i.e. 120 modules), and 2 "Main" inputs: you get a PNom ratio = 1.25, quite correct.

4. - There are 35 modules left to be attributed. This will correspond to 2 different "Secondary" inputs, so you have to increase the number of sub-array to 3.

5. - Sub-array #2, define 1 "secondary" input, and attribute 18 modules.

6. - Sub-array #3, define 1 "secondary" input, and attribute 17 modules.

7. - Now the Warning "The inverter power is strongly undersized" appears in red, because the Overload loss is over 3% (depending on the meteo). You have to increase the "Limit overload loss for design" in the project's definitions.

Now your system is ready for the simulation.

_________________
Best regards | Cordialement
Lazare Fesnien – www.pvsyst.com


Top
   
 Post subject: Re: unbalanced MPPT
PostPosted: Thu Mar 25, 2021 11:08 am 

Joined: Wed Mar 24, 2021 10:34 pm
Posts: 11
Thank you so much for the perfect explanation.
Just I have small question related to my design , I have followed your instruction and the design seems to me ok but I have got message " the array MPP voltage may not attain the inverter minimum voltage for full power" , so does this mean I have problem in my design and how I can solve it ?
Thank you for your Patience


Attachments:
Capture.PNG
Capture.PNG [ 361.2 KiB | Viewed 267 times ]
Top
   
 Post subject: Re: unbalanced MPPT
PostPosted: Thu Mar 25, 2021 8:28 pm 
User avatar

Joined: Tue Oct 18, 2016 3:31 am
Posts: 348
You should increase the number of modules in series.


Top
   
 Post subject: Re: unbalanced MPPT
PostPosted: Thu Mar 25, 2021 9:21 pm 

Joined: Wed Mar 24, 2021 10:34 pm
Posts: 11
Yes , I have increased number of modules and the problem solved , thank you


Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 5 posts ] 

All times are UTC+02:00


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Limited