To force a PV Component for a simulation
https://forum.pvsyst.com/viewtopic.php?f=23&t=244
Page 1 of 1

Author:  Jérémy [ Thu Oct 25, 2012 12:10 pm ]
Post subject:  To force a PV Component for a simulation

Hi,

I would like to simulate a PV plant where the DC VoC voltage is superior to the maximum DC input voltage of the inverter. the over voltage would be only 12 V more, with a flatroof installation.

Yet the software doesn't allows me to simulate it.

Are there any possibilities to overpass the software restriction and to get the simulation done?

thanks.


Jérémy

Author:  Rapha123 [ Thu Nov 08, 2012 10:49 am ]
Post subject:  Re: To force a PV Component for a simulation

There are two ways, you can change the minimum temperature in Project -> Site and Meteo -> "Lower temperature for VmaxAbs limit. Chaging from -10C to a say -5C will then work. The actual minimum temperature depends on the site location.