kjs55 Posted April 20, 2022 Posted April 20, 2022 Hi, It looks like the option to apply a grid power limitation at the inverter level vs. injection point is an EITHER/OR. But, what if we have limits at both the inverter level AND the injection point? It doesn't look like we have the option to apply losses at both points (nodes) in the system (it's only EITHER/OR, not AND). I suggest adding the AND option. Thanks.
André Mermoud Posted April 21, 2022 Posted April 21, 2022 At the inverter level, there is a first limitation, which is the nominal power of the inverter. If the Inverter's power limitation is attained (before the grid limitation is applied), it is accounted as inverter overload loss. When the the grid limitation occurs, in practice it is executed by limiting the power at the output of the inverters. The corresponding power loss due to the grid limitation is accounted a grid limitation (unused energy). This requires that the "grid power measurement" information has to be included as input to the inverter, for adjusting its real output power. Now applying the grid limitation "at the inverter level" means that this required grid power limit value is evaluated at the output of the inverters. This means that the AC losses after the inverter are not taken into account, i.e. that the effective power at the grid level will be (Grid limit - AC losses).
dtarin Posted April 30, 2022 Posted April 30, 2022 The purpose would be to allow the inverter to be limited below nameplate power (which is not uncommon), and also allow a grid limitation to be applied at the POI. This is easily implemented in excel, and should also be able to be implemented in PVsyst.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now