Jump to content

Problem in the design


Abdel

Recommended Posts

Hi,

I have problem in my design but I don't know what is exactly the problem , the system consists of 154 KW DC power (Longi 370W PV modules) with 3 Sunny Tripower core 1 inverters of 50 KW (total 150KW).

As shown in the error message " The array Voc at -27 is greater than the inverter absolute input voltage". the location of the design is located in Finland and in winter the temperature can reach until -30 , so I can't rise the temperature.

When I tried to decrease the the number of modules in series , the system gave me error message "8 inputs with 1 string and 10 inputs with 2 strings , Consider disabling use of multi-MPPT feature for ensuring power sharing on each input"

So , Can PVsyst team help me with any hint to solve the problem ?

Capture.thumb.PNG.d332e7f0d41bb4cbdc52bbbfbf578d7d.PNG

Capture.thumb.PNG.1f5a7fd21a1b155f5274a7473bed377a.PNG

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...