cyoung Posted November 13, 2020 Posted November 13, 2020 I'm simulating an off-grid system with a battery and backup genset but i cant figure out how to change the SOC trigger level for the Generator Startup.In the PVsyst Report this is listed as "Battery Management Control" "Back-Up Genset Command SOC = 0.15/0.45"I interpret this as start generator at 15% and stop at 45%I would like to change this to start at 30% and stop at 55% to reduce battery wearHow do i change this?Thanks
cyoung Posted November 23, 2020 Author Posted November 23, 2020 Answered my own question,The settings i was looking for are under Main Parameters --> System --> PV Array Tab --> Controller (Open) --> Thresholds Tab
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now