PostPosted: Wed Jun 27, 2018 7:21 pm 

Joined: Tue Mar 12, 2013 9:23 pm
Posts: 8
I am modeling a large tracker array with a 12.47kV interconnection voltage. When I select "From transfo to injection" and enter 12470 in the Vac parameter, the "Iron loss" parameters automatically jump to *4700% and *41788 kW. Additionally, an error message pops up. See the attached screenshot. I have tried selecting different voltages, but still get a conversion error in the Iron loss parameters.

I'm running the latest version, V6.73 on Windows 10.


Attachments:
PVsyst Error.jpg
PVsyst Error.jpg [ 223.95 KiB | Viewed 239 times ]
Top
   
PostPosted: Fri Jul 06, 2018 11:04 pm 
User avatar

Joined: Mon Apr 16, 2012 7:29 pm
Posts: 1460
Yes sorry, this is a stupid bug in the version 6.73, which will obviously be corrected in the V 6.74.
In the meanwhile, the only way for correctly defining this parameter is to revert to the previous version 6.72.


Top
   